TallGirl, yes, micros are great for those accustomed to ac wiring only and also great for contractors who hate math.
Lots of those.
I love math and can do the calcs.
Ok, i don't really know how sensitive they are, i will trust your expertise.
The fact remains that, that would be very hard work on a steep roof.
And i will be up there. So i will use a string inverter in this case.
I do, and have, applied micros where it makes sense.
For example, some jurisdictions have onerous req.s for dc discos.... which i just skip if i have micros.
Some roofs are easy to work on.
Some systems are small. I will make great use of the new SMA micros on a 1.5 KW array.
GGUNN, and TallGirl, i appreciate the warning on 5 panel strings. Those are impossible.:happyno:
Agent Moller and Jben, funny thing is: that is exactly what i will do, 2 @ SMA SB4000TL-US inverters.
10+10 on one.
10+6 on the other.
It is in fact 2 @ 25 A brkrs===>50 A brkr needed.
In terms of the 50 A vis a vis the 200 A MSP,
I will either see if it flies per inspector (actual amps of 33.3 A BUMPED UP TO 125% CONTINUOUS ARE ONLY 41.6 A)
or i will downsize the main brkr to 175 A, from 200 A.
I really don't care what the customer decides to do with the 200 A main breaker i will leave with him after I finish.....
I know my labeling of pv breakers ("DO NOT RELOCATE") and breaker placement opposite feed, and actual amps are all within safe limits.
That is because if there were a dual-MPPT, 7600 Watt inverter (max amps 32A) i could easily hook up this 9 kW array to it.