I think building 2 just has two service disconnecting means and doesn't feed the first building in any way.I don't understand the disconnect for the house at the second building? That is unnecessary. You could have run directly to the second building panel
Valid question. We must clarify if it indeed is one service or if it is two services to two buildings. The fact that there is a meter there doesn't make it one service as far as the NEC is concerned, but it is one service as far as the POCO is concerned. But that said the "service point" is likely either at the load side terminals of the meter or somewhere closer to the source. Then there is 230.40 exception 3 as mentioned below, but I do have some additional commentary on that one in the OP's case.What about the issue of grouping the disconnects. Since this is one service, should they be grouped at a common location making this installation non-complying?
Being that this is a single-family dwelling, 230.40 Exception No. 3 allows the service drop to supply a set of service entrance conductors for each structure. Each set of service entrance conductors permitted, in this case two, may have up to two to six disconnects grouped at a common location. There is no need to have a disconnecting means at the first structure for the service conductors supplying the other structure.
Same here, and I have installed very similar arrangements before, especially on farm places. POCO puts a meter on a pole, pedestal, or whatever and all other buildings on the place have service conductors run to this point. They usually also have a disconnect, but inspectors here do not call it the service disconnect even if it has overcurrent protection, as POCO usually controls it and can (and does) replace it with one that has no overcurrent protection.To me, the install as shown is Code compliant.
If this is 2 separate houses (not an auxilary building), though maybe on one property, I wonder if the possibility exists for the houses to be sold to separate owners in the future by subdividing the property parcel. Of 12 years on local zoning board in my town I have seen things like that happen many a time. An applicant would gain approval to build a second house, swearing it was for elderly relatives coming to live with them forever, then a year after approval is granted to subdivide and build a second house, unforeseen family conditions arise and whoops, up goes 2 for-sale signs.
Commercial properties are more notorious for that kind of whoops. I think a lot of individuals have things pre-planned.
**Just wondering.. Has that AHJ commented upon any concerns of that nature, as it may lead to neighbors negotiating an electric bill sharing each month or feeders becoming services and crossing property lines.
Example: In a next town over, zoning variance was achieved for a 2 story commercial structure where it shouldn't have been. (That's the job of zoning and planning boards to evaluate and approve or deny such variances from the allowable.) To leave this place anonymous, I'll just say a clothing store was going to be going in there. Yes, a 2 story commercial building with 2 separate wings on each floor and center atrium. I said to a pal, watch that place, they'll split it into multiple businesses. For a single clothing store, I thought it odd when I passed there one day and noticed a new 6-meter bank on the side of the building. Of course the original applicant ran into unexpected financial trouble and want back to zoning/planning board for a sob story to now split the place into multiple businesses "after" the entire structure had been built, of course.
When I saw the original new single meter pan and riser changed to a 6-banger, I told my pal I should have laid a bet on that situation happening.
Drake,
Old Bridge, NJ
I think you have to get past 230.40 before 230.71 can be applied