Just curious to everyones thoughts on the proper column to size your wire from? I would love to use 90 degree column is this correct. My base wire is thhn/thwn-2 for 250 amp sub-panel i would use 4/O indoors.
Take a look at 110.14(C).
I dont understand what they mean by not to exceed lowest temp rating of any connected termination, conductor or device? So if a sub panels terminals are rated 60degrees I have to size wire to that? I dont remember ever seeing that on the panel label but then again I never looked for it. I always thought it was for temperature the location the wire was ran in. Whats the standard terminal temp for panels if any?
I dont understand what they mean by not to exceed lowest temp rating of any connected termination, conductor or device? So if a sub panels terminals are rated 60degrees I have to size wire to that? I dont remember ever seeing that on the panel label but then again I never looked for it. I always thought it was for temperature the location the wire was ran in. Whats the standard terminal temp for panels if any?
so its 75degrees for 100 amps and over #1 or larger. in what instance would you use the 90degree column then?oops read further i see
so its 75degrees for 100 amps and over #1 or larger. in what instance would you use the 90degree column then?
That's it. If they're 75? C then you can use the 75? C ampacity. For all intents and purposes 90? C is only a starting point for derating.
good to know. I never used it to derate what about continuous load factor ? could I use 90 degree then?