CT wiring classification
sketchy
MN
What would a current transformer's wiring be classified as? Is it a communication circuit? I have to run ct wires for long distances, longer than the factory wiring. I'm trying to find a cable to run through existing conduit, I.e. a 2" conduit with 3/0 copper, that is rated for use with the 240 volt conductors, thus avoiding making another penetration in the home. I found a 22 gauge FPLP/760, CMP/800, CL3P, CL2P/725 rated for 300 volts. Would this be legal to run with 240 volt circuits?
It is extremely unlikely that any wire size smaller than #14AWG will provide reasonable performance at distances >50'.
This is basically a voltage drop problem, you need to determine if your CT's can handle the resistance of your leads + the metering equipment. The math is relatively easy, getting the proper equipment parameters can be much more of a problem.
Your CT supplier should be able to help you.
If the distances are really great, you could consider a CT transducer, where the 5A output is converted to a 0-20mA signal. This would allow you to follow Class 2 'communication' wiring practices.
I've run cat 5 400' without a problem. My issue is finding a cable that is legal to run with the existing 240 volt wiring. The ct wires are class 1. I need a cable that is class 1 as well.
The issue is the output power of the CT.
You mention 3/0 copper, so I could guess you are using a 200:5 CT. A typical burden capacity for an inexpensive metering CT will be at most 5VA, which equates to a load of roughly .2 ohms.
If you use #14AWG you might be able to get to 40' as long as you are using a low impedance meter or electronic load, before your CT is overloaded and its output becomes 'inaccurate'.
Slow poster - following jim's comment
Sketchy -
I can't help, but I am kind of curious:
22 gauge is ~ 16ohms/1000ft. For 400 feet, 800 feet round trip, that's 12.8ohms. For a 5A CT, that's a 64V drop - about 320VA. And you would have to add the burden of your end device. Are your CT rated for that kind of a burden?
Most CT I've seen are usually rated 2VA - 10VA, a few rated up to 35VA.
What kind of accuracy do you see with 400 feet of cat 5?
Just curious
ice
It would be my opinion that the CT wiring would be an Article 725 Class 1 circuit.
A question that seems to have been bypassed is what the voltage on the CT output leads will be if they are left open-circuited. That may have a bearing on the choice of wiring method, even with limited power.
The open circuited CT is just a voltage step up transformer with a weak core which will saturate at some point. You are counting on that core saturation to limit the Voc under load.
A standard commercial CT will likely not have an open circuit voltage above 25V or so, but it is worth confirming for the CT you are specifying.
As far as accuracy, I can't answer that. It was for a company I used to work for. We would run a cat 5 accross an entire target store from the service to a monitoring panel. 400' might be an exageration, 300' for sure. This particular application is for monitoring solar production. I ended up using a pair of TFFN wires.
just curious.
The cat 5 across an entire target store really sounds line a transducer output - not a 5A CT output. do you recall?
This TFFN pair you used - How far was that?
ice