Hello all, I have been reading Q @ A's for years and definitely added to my knowlege base from some of the answers. I have been working on an ongoing issue for months now and figured going to the broad knowledge base here was a much needed step. I will try my best to explain the entire issue in this post but any additional questions would be appreciated and answered quickly....
The biggest of our warehouses is a little over 1,000,000 ft^2, around the exterior of the building are about 15 remote PIV units. On the interior of the building the IDC circuit goes to a single or duel mod, then to a surge protector, out + or- 150ft to the PIV which has a module that we hook to the normally open contacts with a 47K resistor, which is then obviously hooked to a micro switch inside the PIV.
The issue is we go into supervisory for these PIV's every week, so far as I have about 5 of them shortened to eliminate the piv module. The microswitch is definitely open, but is still sending the system spontaneously into alarm. Now we've replaced the modules inside the PIV's thinking maybe the damp conditions, and the microswitches even though Ahern and I said they were fine.
My first question is does somebody think moving the suppressors from the load side of the mod going outside to the line side of the mod could possibly solve the issue? or is this wishful thinking. I understand this would no longer protect the mod from lightning strikes or surges, but replacing a few modules is much cheaper than continuing to troubleshoot these alarms.
Or.. Changing the module to a normally closed state and monitoring the PIV's that way? I understand if there is a short between the wires I would not get a trouble alarm, but we do quarterly checks on the PIV's. I am assuming I would have to check with the insurance company and local codes first, but this issue just doesn't seem to go away. Has anyone else had an issue like this? or any ideas on a possible reason for this would be appreciated. Thanks for any help, sorry for the long first question.
Brandon
The biggest of our warehouses is a little over 1,000,000 ft^2, around the exterior of the building are about 15 remote PIV units. On the interior of the building the IDC circuit goes to a single or duel mod, then to a surge protector, out + or- 150ft to the PIV which has a module that we hook to the normally open contacts with a 47K resistor, which is then obviously hooked to a micro switch inside the PIV.
The issue is we go into supervisory for these PIV's every week, so far as I have about 5 of them shortened to eliminate the piv module. The microswitch is definitely open, but is still sending the system spontaneously into alarm. Now we've replaced the modules inside the PIV's thinking maybe the damp conditions, and the microswitches even though Ahern and I said they were fine.
My first question is does somebody think moving the suppressors from the load side of the mod going outside to the line side of the mod could possibly solve the issue? or is this wishful thinking. I understand this would no longer protect the mod from lightning strikes or surges, but replacing a few modules is much cheaper than continuing to troubleshoot these alarms.
Or.. Changing the module to a normally closed state and monitoring the PIV's that way? I understand if there is a short between the wires I would not get a trouble alarm, but we do quarterly checks on the PIV's. I am assuming I would have to check with the insurance company and local codes first, but this issue just doesn't seem to go away. Has anyone else had an issue like this? or any ideas on a possible reason for this would be appreciated. Thanks for any help, sorry for the long first question.
Brandon