Just wondering what others have done. Siemens panel with Siemens type BL breakers. I have some of the fingers on the buss that have stripped out. On A and C phase looks like the fingers will be easy to replace. On B phase it appears to be more of a bear. I have seen on a couple spots someone has used ground screw (10-32). I am planning a shut down to take care this and do it right, but that wont happean untill Thanksgiving weekend. Is there any tricks i can do, drill and tap to get by untill then. Thanks
By do it right , do you mean ordering new guts for the panel. If it's not to old that is likely the best option. Considering of course the load.
Just for conversations sake. What type of load will be in these positions? HVAC, Lights, Motors making medical equipment, are they continuous loads. (20. 30 100 amps)
And your job is to save the company money.
Even if the facility is running 24 hours a day. I would think you could order the parts and get every thing ready.
With a little help and the same brand guts to the panel as the breakers. If the new guts fit, it's possible to change it out in an hour or so . Unless it's a huge swiich gear.
The wires would not have to be loosened on the breakers. Just unbolt them. Replace the guts with a ul approoved bus bar (guts just bolt in). Then bolt the breakers back and your good to go.
It might even be safer because you would not be working on a live bus bar. And I know how close those phases are. I just worked on one today.
It feels kind of weird to unscrew live breakers with a makita impact drill. Although the drill is mostly plastic. Their are some recessed screws in the handle. Put some Scotch 33 over them.
I don't know how old you are. But have you have seen the "Creature of the black lagoon" Well he/it was a victim of an arc flash.
You would have to have watched the first episode to know that. Of course I wached it on a rerun because I'm not old
Another option would be to install a small cheap sub panel beside it until Thanksgiving.