Lightning_Strikes_Twice
Anyone ever use MTW?  I am wondering what restrictions for the terminal side there are? If i am taking this to a breaker is there a particualr type of lug for this wire, or will it behave like THHN?
Anyone ever use MTW? I am wondering what restrictions for the terminal side there are? If i am taking this to a breaker is there a particular type of lug for this wire, or will it behave like THHN?
I am not even sure it is a type of insulation allowed by the NEC.
It is my opinion that the "application provisions" of that table limit the use of MTW to wiring that is part of a machine tool, unless the conductor has additional markings on it.Table 310.104(A) tells us what 600 volt or less insulation types are permitted by NEC - MTW is in there.
Yes that is true, but it does not behave like real MTW as far as how it looks when you wire a panel. Most of the MTW used for panel wiring is not dual rated and not suitable for NEC applications.I thought alot of the dual rated thhn /thwn was also mtw rated. I have seen it on some larger wires at our supply company