Thanks augie47,
I am an old electrician by trade but my job has me doing a lot of non electrician stuff. I looked at NEC section you sugested. I looked at the definition of Controller:
Article 100 definitions
Controller. A device or group of devices that serves to govern, in some predetermined manner, the electric power delivered to the apparatus to which it is connected. A controller may be a remote-controlled magnetic contactor, switch, circuit breaker, or other device that is normally used to start and stop motors and other apparatus and, in the case of motors, is required by 110.9 and 430.82 to be capable of interrupting the stalled-rotor current of the motor. Stop-and-start stations and similar control circuit components that do not open the power conductors to the motor are not considered controllers.
I think that definition fits my electrical cabinet. Inside I got: fuses, motor starters, relays, PLC processor and it's I/O - all for controlling conveyors. The only thing I am missing is a disconnect switch mounted directly on outside, of previsiosly mentioned, panel.
I also found this wording; "Industrial facilities that comply with OSHA, 29 CFR 1910.147, The Control of Hazardous Energy (Lockout/Tagout), are permitted to have the disconnecting means located remotely. (DOES THIS APPLY TO ME?)Section 430.102 clearly requires that individual disconnect switches or circuit breakers must be capable of being locked in the open position. Disconnect switches or circuit breakers that are located only behind the locked door of a panelboard or within locked rooms do not comply with the requirements of 430.102. The provision for locking or attaching a lock to the disconnecting means must be part of the disconnect and a permanent component of the switch or circuit breaker."
I think I am Legal and safe based on what I read in 430.102 - what do you think??