Hypothetically speaking:
Instruction ask for #12 AWG with 1/2" EMT but you do the installation with #10 AWG & 3/4" EMT.
Is this in violation of 110.3?
Or if the plans were approved with 1/2" & #12 AWG but the installer installed 3/4" EMT with #8 AWG. Can the inspector cite 110.3 and fail the inspection?