bjp_ne_elec
- Southern NH
Got a service call to look at a generator that had to be moved.  Turns out the original LP vendor hooked up the generator too close to house.  There was only about a one foot space.  New LP vendor comes in, and good for them, want it corrected before they replace existing tank.
There are two 14/2 circuits and then the 50 amp circuit that the generator will be feeding. The original electrical job was evidently not inspected as I find the 3 wire 50 amp and the two 15 amp (one is a 240 volt and the other is a 120 volt) all stuffed in a piece of sealtite and the end inside the basement is not terminated in to a JB) Should have taken pics, but did not.
The 240 volt circuit is for remote sensing the utility power at the generator, and I need to check the installation guide to see what other circuit is for, but it was not powered when I checked it. The one sensing utility power was actually hot. Should each of these 15 amp (actually fused at 2 amps in the control panel) have a disconnecting means at the outside, near generator?
Another question I have is how you guys configure the outside wiring. I was thinking of putting a WP trough on the outside face of the house and then, bringing in the 8/3 and the two 14/2 Romex in to the back side of the trough, and then just running a 1" PVC to the generator. The trough would allow me to pull everything together, allow me to make up joints ( 14/2 needs a place to make up joints), and then connect to the gen.
If anybody has some pics of how they lay something like this, I'd love to see them.
Thanks
Thanks