sparkycoog
Member
- Location
- Texas
I have run across this question a couple of times now and I'm pretty sure I have missed it each time, but can there ever be a 7th disconnect? 230.2A 1-6 does allow for a second service (like for fire pumps parallel power, etc) but sections 230.71 and 230.72 are very strict in the wording that a max of 6 shoukd exist and out of the 2 to 6 only one of the can be located remotely. So again, is there any room for interpretation to allow for one more? The reason I ask is because in Mike Holt's exam prep book, on page 133 figure 5-24 he has a 7th disconnect which is a PV disconnect and I'm sure it's not an accident.What's the good word?