moorekeith99
Member
- Location
- Austin Texas
Is there a correlation between a 3 phase motor that went bad and a un-bonded 4000 amp service. I have a 4000 amp 277/480 volt service that was not bonded. There has been one chiller motor 3 phase 3 wire with ground (480) and a condenser motor 3 phase 3 wire with ground (480) that has gone bad. The mechanical contractor says it is because of the service being unbounded. I believe unless it is something that requires a neutral that should not have been a issue. Please comment as I have a conference call at 0100 pm today pertaining to this issue. I would appreciate any and all ideas on this issue. Also the transformer behind this serviced were bonded and grounded properly. Will the no bonding on the primary side create any issues with the secondary side of transformers behind this service. Since they are separately derived systems I would think not.