Have a friendly discussion in the office on this one but trying to work out the math part of it. With a MWBC [typically for lighting] I see a lot of 277V fixtures connected to a 480Y/277V MWBC with the thought that the voltage drop is lower compared to dedicated neutral circuits. If the loads are connected as 277V L-N how is the VD any different? If you calculate it at 480V-3Ph you can definitely extend the circuit or add fixtures to remain within a recommended percentage, just trying to figure how when connecting 277V L-N fixtures on a 480Y/277V ckt. the VD changes? :?