348.30 - FMC for Chain Suspended Fixtures

Status
Not open for further replies.

kevdog

New member
Location
Baltimore
Details of the project:
  • Location: Open Boiler Plant
  • Chain Lengths from Ceiling Support Structure: About 12'-0"
  • 600V and Below

My first inclination would be to recommend that SJO or STO cable be fastened and run along the chain support to the light fixture termination.

However, STO cable would require a deviation from the project specification, which calls for FMC in this application.

Would it be code compliant if I:
  • run conductors for fixture in FMC with an EGC down the 12'-0" vertical run
  • and securely fasten the FMC to the chains supporting the light fixtures (within 1' of the juction box at the ceiling and every 3' or so down to the fixture)

Any help or suggestions of other ways to accomplish this task is much appreciated.

Thanks
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Would he need stranded MC cable?

410.56 Protection of Conductors and Insulation.
(E) Stranding. Stranded conductors shall be used for wiring
on luminaire chains and on other movable or flexible parts.
 