131002-1245 EDT
A simple experiment. One 26 W CFL (non-linear load) and one 15 W incandescent (resistive load).
123 V and a Kill-A-Watt instrument.
Actual measurements.
CFL --- 0.27 A, 23.4 W, 33.8 VA, 0.69 PF
15W -- 0.12 A, 15.3 W, 15.3 VA, 1.00 PF
Both -- 0.37 A, 38.6 W, 45.9 VA, 0.84 PF
Conclusions:
= 38.7 vs 38.6 . Fairly close.
Voltage varied somewhat and CFL has some instability. But, it is clear that you can not calculate total current from the 23.4/123 = 0.19 and add 0.12 and get 0.37 . Also, you can not just add 0.27 and 0.12 and say these are the total current. You must know the waveform and calculate from the waveform.
It is interesting that :
216/208 = 1.04
260/208 = 1.25
270/208 = 1.30
and
(0.27+0.12)/( (23.4+15.3)/123 ) = 0.39/0.31 = 1.26
This supports my guess that 260 might be a possible answer. When guessing I was not expecting to be that close to some actual measurement.