208Y/120 three phase house meter. Owner wants three MWBCs from house meter transferred to one of the suite's single phase panel. Found first JB where Phase A spits off with a neutral and feeds outlets. Phase B & C pass through.

Couldn't we refeed Phase A with it's neutral to the single phase suite panel and also interrupt Phase B & C at this JB with its neutral and refeed it also to the single phase panel as a MWBC?
__________________
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
208Y/120 three phase house meter. Owner wants three MWBCs from house meter transferred to one of the suite's single phase panel. Found first JB where Phase A spits off with a neutral and feeds outlets. Phase B & C pass through.

Couldn't we refeed Phase A with it's neutral to the single phase suite panel and also interrupt Phase B & C at this JB with its neutral and refeed it also to the single phase panel as a MWBC?
__________________

I don't see why you couldn't.
Just use a 2 pole breaker on the MWBC.
 