NM usage non usage question.

Status
Not open for further replies.

ritelec

Senior Member
Location
Jersey
Reading through the permitted and not permitted usage of nm.........

Did the article about a third or half the basement being above ground level leave?

I will be doing some work in a single family... 1/2 basement is above ground.. 1st and 2nd floors, and attic is somewhat finished.
The way I see it nm is permitted for use. Correct me if I'm wrong please.

Also 334........ is that for nm-b also? whats the b for?

Also also......protect from physical damage, 334.15 (B)......Schedule 80 pvc?????? Schedule 40 is not permitted???

Also also also... supports.......12" to a box ..... looks to me that thats for all boxes, metal or plastic.....did they get rid of the 8" to plastic box
with no clamp or connector?

Thank you.
 
Last edited:

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Not sure of your reference to 1/2 below grade.

NM is NMB. I don't know what the B is other than it was designated back when NM became 90C
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Not sure of your reference to 1/2 below grade.

NM is NMB. I don't know what the B is other than it was designated back when NM became 90C

The question, I think, is how much has to be below grade (level or on a hillside) to make the difference between a ground floor and a basement.

Outside the US, NM (no B) is still available and usable with the lower temperature rating, AFAIK.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The question, I think, is how much has to be below grade (level or on a hillside) to make the difference between a ground floor and a basement.

Outside the US, NM (no B) is still available and usable with the lower temperature rating, AFAIK.

I don't think it makes a difference. I could tack wires up on a first floor exposed as long as it is protected. Not sure what the issue is specifically
 

Gregg Harris

Senior Member
Location
Virginia
Occupation
Electrical,HVAC, Technical Trainer
STORY ABOVE GRADE PLANE. Any story having its finished floor surface entirely above grade plane, except that a basement shall be considered as a story above grade plane where the finished surface of the floor above the basement meets any one of the following:

1. Is more than 6 feet (1829 mm) above grade plane. 2. Is more than 6 feet (1829 mm) above the finished ground level for more than 50 percent of the total building perimeter. 3. Is more than 12 feet (3658 mm) above the finished ground level at any point.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
STORY ABOVE GRADE PLANE. Any story having its finished floor surface entirely above grade plane, except that a basement shall be considered as a story above grade plane where the finished surface of the floor above the basement meets any one of the following:

1. Is more than 6 feet (1829 mm) above grade plane. 2. Is more than 6 feet (1829 mm) above the finished ground level for more than 50 percent of the total building perimeter. 3. Is more than 12 feet (3658 mm) above the finished ground level at any point.
Helpful!
So, I guess I could make any basement a story above grade plane by digging and finishing a 12' deep pit next to its perimeter at any point? Even if the bottom of that pit is 6 feet below the basement floor. :)
 

ritelec

Senior Member
Location
Jersey
I have to look for some older books..but like 15 or 20 yrs ago.......... nm was not allowed in buildings over three stories......and the first level was considered the basement
if 1/3 or 1/2 was above finished grade.........
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
I have to look for some older books..but like 15 or 20 yrs ago.......... nm was not allowed in buildings over three stories......and the first level was considered the basement
if 1/3 or 1/2 was above finished grade.........
If it said three stories above grade plane, then the definition that Gregg Harris posted would be the key.
 

Gregg Harris

Senior Member
Location
Virginia
Occupation
Electrical,HVAC, Technical Trainer
I have to look for some older books..but like 15 or 20 yrs ago.......... nm was not allowed in buildings over three stories......and the first level was considered the basement
if 1/3 or 1/2 was above finished grade.........

336.4

1993
removed 1996
 

ritelec

Senior Member
Location
Jersey
Thanks GoldDigger.......

My question is more in the vain of The schedule 80 being mentioned and not the 40.

I've installed 40 and have seen maybe thousands of installs with 40..........
Were my installs (and all other peoples installs, some inspected, some not) not to code????

Never knew only "80" was permitted.......??? Doesn't sound right.

??? lets say, I have nm.......... I have a run.....I then install a box (or not) and sleeve it in 40. WRONG?
??? lets then say I have nm.... I have a run.....I then install a box and sleeve thhn/thwn in 40. RIGHT?
 

Gregg Harris

Senior Member
Location
Virginia
Occupation
Electrical,HVAC, Technical Trainer
Thanks GoldDigger.......

My question is more in the vain of The schedule 80 being mentioned and not the 40.

I've installed 40 and have seen maybe thousands of installs with 40..........
Were my installs (and all other peoples installs, some inspected, some not) not to code????

Never knew only "80" was permitted.......??? Doesn't sound right.

??? lets say, I have nm.......... I have a run.....I then install a box (or not) and sleeve it in 40. WRONG?
??? lets then say I have nm.... I have a run.....I then install a box and sleeve thhn/thwn in 40. RIGHT?

Nothing precludes the use of schedule 40, unless it is deemed in an area that is subject to "physical damage"

(B) Protection from Physical Damage. Cable shall be protected from physical damage where necessary by rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80 PVC conduit, Type RTRC marked with the suffix -XW, or other approved means. Where passing through a floor, the cable shall be enclosed in rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80 PVC conduit, Type RTRC marked with the suffix -XW, or other approved means extending at least 150 mm (6 in.) above the floor.
 

ritelec

Senior Member
Location
Jersey
Nothing precludes the use of schedule 40, unless it is deemed in an area that is subject to "physical damage"

(B) Protection from Physical Damage. Cable shall be protected from physical damage where necessary by rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80 PVC conduit, Type RTRC marked with the suffix -XW, or other approved means. Where passing through a floor, the cable shall be enclosed in rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80 PVC conduit, Type RTRC marked with the suffix -XW, or other approved means extending at least 150 mm (6 in.) above the floor.

yeah.............wow.............

A switch location in a residential application between two garage doors.........(you know what I mean......and similar.whips down basement walls etc...) sleeved in 40 would not fly???

Guess it would be who's interpreting the physical damage? garden tools and equipment, chinese stars or paperclips.......................driveways, runways, or the battlestar galactica.........

wow.........

OK
 