Have a question regarding this table.
I have a 200A 120/240 Volt single phase service that is currently established at a pole barn. I am looking to feed a new dwelling that is being built on the property. In sizing the conductors for a 150A panel located in the house, can I use the #1 CU that is listed in this table or do I need to go to 1/0 CU ? Seems that I ran into this years ago and the AHJ said that once it is beyond the service entrance conductors and the meter base it is a sub feed and no longer falls under this table. The new feed will be coming from a 200A 3R panel via a 150A plug in breaker it will not be feeding directly off the load side of the meter. Thanks much.
I have a 200A 120/240 Volt single phase service that is currently established at a pole barn. I am looking to feed a new dwelling that is being built on the property. In sizing the conductors for a 150A panel located in the house, can I use the #1 CU that is listed in this table or do I need to go to 1/0 CU ? Seems that I ran into this years ago and the AHJ said that once it is beyond the service entrance conductors and the meter base it is a sub feed and no longer falls under this table. The new feed will be coming from a 200A 3R panel via a 150A plug in breaker it will not be feeding directly off the load side of the meter. Thanks much.