I'm looking for feedback on the poor installation standard of connecting single pole loads to multi-pole breakers. I've seen projects red-tagged in the past by inspectors because this type of connection was outside the UL listing of the breaker. Otherwise, I don't know of a code prohibiting the practice.
I have a client with new critical space panels that will only accept 3-pole breakers. The breaker manufacturer will support 2 and 3 pole connections but not single pole connections. The client currently has many instances of multiple single pole loads connected to the same 3-pole breaker. 240/415V
Does anyone in this forum have experience with this issue?
Thank you.