Got a call today from an individual looking for someone to finish electrical work that was started by another contractor.Seems as though other company was fired because of their inability to return and finish the job in a timely manner. With that being said I looked over the work that was done so far and it appeared to be neat. The owner shows me a detached garage that was also wired and provisions for a hot tub. When I get to the service(exterior) I find a 200A 120/240V single phase U/G meter base, it's feeding a 200A MB panel in the house and a 100A MB panel in the garage. The previous contractor appears to have added dual bolt on lugs to the load side of the socket and treated the garage run as under gound service conductors. The inspection tag on the base says approved. What am I missing here, is not the socket undersized for the connected loads that are already wired? Is changing the load side lug configuration acceptable? Thanks.