electrofelon
- Cherry Valley NY, Seattle, WA
- Electrician
Multi-part question here:
1. When installing a service, do you try to set things up so that there is only one neutral-ground bond to avoid a metallic raceway carrying neutral current? Of course this may not be possible with equipment that has a factory neutral to case bond like most meters and some CT cabinets, but say you have a pull box, buss gutter, or trough on a service; would you keep the neutral unbonded and run a bonding jumper back to the service disconnect or use a nonmetallic raceway between them?
2. Have you ever been cited by an inspector for 250.6 for creating a parallel path at a service?
3. The NEC is very specific that a SDS shall have only one bond point (unless the interconnecting raceway is nonmetallic). Why dont they specify the same thing with services? As mentioned, of course this would cause some problems with some meters and CT cabinets, but a non-metallic raceway could be used or the NEC could just say they cant be bonded - they certainly haven't shied away from making manufacturers design equipment a certain way in the past.....Why is an SDS different?