I am confused about section 220.61(C), regarding sizing the neutral in this particular application.
480 vac 3 phase 4 wire, with neutral to metering compartment only where it is dead-ended and grounded by the utility. We then have only 3 phase conductors and ground from metering compartment to our service entrance equipment with no neutral bus. We have a VFD, which constitutes about 50% of the load.
Since there is no neutral in our service panel and no loads connected to a neutral, I don't see how I can have any current in the neutral conductor from the meter can to the transformer. So it seems that this neutral could be reduced to 50% since it is not used.
Is this correct or have we missed something??
480 vac 3 phase 4 wire, with neutral to metering compartment only where it is dead-ended and grounded by the utility. We then have only 3 phase conductors and ground from metering compartment to our service entrance equipment with no neutral bus. We have a VFD, which constitutes about 50% of the load.