We have a customer adding a 480 v service to power (7) refrigeration units on the back of Semi trailers. The units motors use 25 FLA, with a 99 LRA. Just to clarify we do not have to use the LRA when calculating the service size, correct?
 

StarCat

Industrial Engineering Tech
Location
Moab, UT USA
Occupation
Imdustrial Engineering Technician - HVACR Electrical and Mechanical Systems
Refrigeration Loads

Refrigeration Loads

You need to go with the MAX size as listed on the unit nameplate rather than the MIN for a troublefree install with regards to HVACR loads.
This a golden rule in Refrigeration.
 