shortcircuit2
- South of Bawstin
Its been awhile since we discussed protecting ground mount arrays wiring from readily accessible approach. On ground mount installations is my area they are having fences installed to restrict access. Is there any other solution accepted in your area? Such as maybe a wall of bushes with 1 gate for service access?
I see they added the option of GUARDED to the 2014 NEC.
(A) Wiring Systems. All raceway and cable wiring methods
included in this Code, other wiring systems and fittings
specifically listed for use on PV arrays, and wiring as part
of a listed system shall be permitted. Where wiring devices
with integral enclosures are used, sufficient length of cable
shall be provided to facilitate replacement.
Where photovoltaic source and output circuits operating
at maximum system voltages greater than 30 volts are installed
in readily accessible locations, circuit conductors
shall be guarded or installed in a raceway.