Note that it only says 'raceways' in that section. Cable assemblies it is not required.
110.3b , as I'm sure the cable manufacture requires protection for their cable assemble
OP asked for EMT connector.
I don't think the plastic bushing is required for EMT connectors. At least it is not required in 358.46 as it is in other XXX.46 section.
A good graphic from Mike:
352.46 Bushings. Where a conduit enters a box, fitting, or other enclosure, a bushing or adapter shall be provided to protect the wire from abrasion unless the box, fitting, or enclosure design provides equivalent protection.
I agree with you and Chris. Also if the connector would have an insulated throat or otherwise has edges that will not cause damage to the conductor it is probably designed/listed to not require the added bushing.It is required for conductors 4 and larger by 300.4 as Chris pointed out.