Duncan8943

Member
Location
Lexington
I have an 800 Amp service. I have to install the metering enclosure for the CT's, as well as, power distribution. From the metering enclosure, I supply five (5) 200 Amp automatic transfer switches. The utility will have two runs of 500 MCM for each phase & neutral. What is the easiest way to do the power distribution? I was originally thinking about installing 3/8" thick by 2" wide bus bars with stand off insulators and using mechanical lugs to do the power distribution. Thanks.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I think that some small 800 amp bus detail on the load side of the CT's would work fine.
 