- Connecticut
- Engineer
Doesn't anyone see this as being odd? Triangular stacked cables with proper spacing in an open bottom/top ladder tray are limited to the same ampacity as if they are installed in a conduit? I would suggest that 392.80(a)(2)(d) allows us to use the 75 degree column "in accordance with 310.15(B)."
But what do I know...
Triangular stacked cables with proper spacing are NOT limited to the same ampacity as if they are installed in conduit. For instance, #3/0 would have an ampacity of 245 in cable tray vs. 200 in conduit. What must be coordinated is the terminations. You could not use a #3/0 75deg termination with the higher ampacity. You would need to use a 250mcm termination even though the conductor size is 3/0 to avoid exceeding the operating temperature of the termination.