Is there a code article for electrical rooms requiring emergency lighting?? The only article I can find is 110.34 (D).
Thanks
Thanks
110.26 (D)Is there a code article for electrical rooms requiring emergency lighting?? The only article I can find is 110.34 (D).
Thanks
Is there a code article for electrical rooms requiring emergency lighting?? The only article I can find is 110.34 (D).
Thanks
110.26 does not require emergency lighting only lighting and an electric room would not be considered part of the means of egress.
Is there a code article for electrical rooms requiring emergency lighting?? The only article I can find is 110.34 (D).
Thanks
700.16 Emergency Illumination. Emergency illumination shall include all required means of egress lighting, illuminated exit signs, and all other lights specified as necessary to provide required illumination.
seems it is necessary to provide light in an electric room which is a good arguement for 700.16
And as a matter of common sense, it should also apply to windowless rooms, wherever situated, which contain equipment requiring servicing (which during an outage may well include the equipment room.
Under that broad definition emergency illumination would be required "for attics and underfloor spaces containing equipment requiring servicing" or for any habitable room without adequate natural illimination.
Under that broad definition emergency illumination would be required "for attics and underfloor spaces containing equipment requiring servicing" or for any habitable room without adequate natural illimination.
700.16 Emergency Illumination. Emergency illumination shall include all required means of egress lighting, illuminated exit signs, and all other lights specified as necessary to provide required illumination.
seems it is necessary to provide light in an electric room which is a good arguement for 700.16
And as a matter of common sense, it should also apply to windowless rooms, wherever situated, which contain equipment requiring servicing (which during an outage may well include the equipment room.
So, definitely a good idea. Required or not may depend on code cycle. I think it is more explicit in [2014].
You could always work by the light of the ubiquitous cell phone.
Is there a code article for electrical rooms requiring emergency lighting?? The only article I can find is 110.34 (D).
Thanks
Since I was likely to be the one checking things and turning breakers off and etc., I put emergency lighting in each new electrical room I installed. I guessed that the $50 -- $100 battery E light was a very small percentage when compared to the $1000s in panels and switchgear.
But then thats just me.:ashamed1:
What good is it when it will not be maintained?
I realize what it says can easily be taken to mean just that, but I have a pretty good feeling the intent is not to include required lighting from art 210, but rather to include any illumination required by whatever code or standard is calling for emergency illumination.
Emergency illumination is generally required for egress purposes or for areas where people will be expected to be present during the condition causing the need for emergency illumination. So unless you intend for people to gather in or for them to egress through the mechanical areas you probably don't have to illuminate that area when normal power is lost in most cases.