Motor acceleration model
wpm1
canada
I'm trying to model a motor accelerating from 0 full load speed. The motor data for Rr, Xr, Xm, Rs, Xs, when I start the model gives a much higher current than the LRA data. I am assuming Is=V/Ztotal where Ztotal= Zs+ (Xm*(Rr/s+Xr i)/(Rr/s+(Xr+Xm)i)). Using the impedance data I expect the calculated amps at slip of 1 should match LRA.
The impedance were reported in P.U. which i was never good at. I am using the phase voltage, and the P.U. impedances.
Any advice?
Wpm1...
A difference between using Ohms and Per-Unit occurs when one uses the wrong Base VA! What value did you use?
Regards, Phil Corso
Fixed it. Yes, I was using %R and %X, but using actual voltage, I took the base reference and converted to actual R and X. Acceleration model works now, torques and currents are very close to what I was expecting. Rusty on the P.U. system, Ha Ha.
Thanks.
Wpm1...
FWI, another common error is using the Rule-of-Thumb (ROT), i.e., kVA equals Hp!!
Phil
1 Hp = 746W (0.746kW)
conservative efficiency = 0.9
conservative pf = 0.85
therefore; 1 Hp approx equal to 1 KVA. Granted this is very conservative, but for quick estimating, works quite well.
Any advice?
Are you designing a motor? I also am assuming the the motor example that you are using is 3ph which shows speed torque curves fro start through the knee of the curve to run.'
How would be different than a common NEMA speed torque curve such as a design 'B'?
Then the is the standard CO curve as I can recall which is based upon the wr2 of the load.
Leakage reactance and resistance values of the rotor depend on slip
One cannot use the same rotor resistance and reactance of steady state run in order to calculate the start current. Leakage reactance and resistance values of the rotor depend on slip . The rotor frequency is elevated at start and reduced in steady state run. That means Rr(slip=0.05)<Rr(slip=1) due to skin effect. See[ for instance]:
http://piers.org/piersproceedings/d...ycmFrZXNofDNQOF8xNDUxLnBkZnwxMDA5MTUwOTU5NTQ=