Bonding of service raceway

Status
Not open for further replies.

faraday2000

Member
Location
fl
Hi can anyone clarified if only one end of the service raceway have to be bonded. Can I bond both ends?

250.92 says service raceways must be bonded but doesn't say if both ends must be bonded or at least one must be bonded.
 

iwire

Moderator
Staff member
Location
Massachusetts
Thanks that what i thought. I just read somewhere in the web that you have to bond both ends and get me confuse.

No problem at all.

Let me suggest this, always look things up in the book yourself. There is a lot of misinformation out in the world sometimes it is deliberate but most times the people are just mistaken.