Pat Beaird
How do you install a branch circuit that requires an AFCI breaker? Why does the code require that the branch circuit wires be installed in conduit between the breaker panel and the first outlet?
Welcome to the forum! :thumbsup:
I am not totaly sure of your question.
AFCI circuits do not have to be in conduit, That is an exception until the first outlet.
By the way what kind of work do you do?
What is this exception? (Is it from the 2014 NEC?....I'm still under the 2008)
From 2008
Exception No.1 Where RMC, IMC, or steel amored cable, Type AC, Meeting the requirements of 250.118 using the branch circuit between the branch-circuit overcurrent device and the first outlet, it shall be permitted to install a combination AFCI at the first outlet to provide protection for the remaing portion of the branch circuit.
thanks for the clarification. Pat BeairdThe basic requirement of 210.12 is that for the specific rooms listed in the article, you must provide AFCI protection for the entire circuit. If you use an AFCI circuit breaker, you clearly will be protecting the entire circuit. But if you instead want to use a normal circuit breaker, and if you want to install an AFCI device at an outlet box some distance from the branch circuit panel, then the portion of the circuit between the breaker and the outlet box will not be protected by the AFCI device. That is, in this type of installation you are not protecting the ENTIRE circuit. But there is an exception that allows this type of installation. The exception says that the AFCI device must be installed at the very first outlet box in the circuit. It also says that you must use one of the conduit types that have already been mentioned. The idea here is that there is a very low risk that an arc fault would take place within the conduit, since the conduit will be protecting the wires from physical damage.