Receptacle rating
cppoly
New York
An appliance cut sheet says it requires a dedicated 15 Amp dedicated outlet. Is a 15 A simplex receptacle required or can a 15 A duplex receptacle be used knowing that only this one appliance will be plugged into it?
The only thing I can think of is a 15 ampere circuit limits the max load of the cord and plug load to 12 A, so while the unit draws 10 A that leaves a maximum of 2 A load allowed if someone plugs something else in to another receptacle if a duplex is used. Also, since the wording in the cut sheet says 15 A dedicated outlet, doesn't that mean a simplex is required because of the word dedicated?
It is a good question. We have an inspector around here that requires a single recep. for microwave range hoods. Because someone can plug something in does not mean they would.
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit.
A single receptacle installed on an individual branch circuit
shall have an ampere rating not less than that of the branch
circuit.
I don't think this requires a single receptacle however I would install a single recep. in the op's case just not sure it is required
Neither the phrase "dedicated outlet" nor the phrase "dedicated circuit" appears in the NEC. I think you can install a duplex for this application.
Just a point of interest- dedicated circuit appears one time in 705.12(D)(1)-- obviously nothing to do with the op's concern
Really Dennis --Outlet.
A point on the wiring system at which current is
taken to supply utilization equipment. -
time to look up dedicated since it is not in the code -- Dedicated 15A outlet = dedicated 15a branch circuit to serve the equipment - the OP wanted the meaning of the manufactures requirement -- outlet & receptacle are two different definitions
Sorry but I have no idea what you are trying to say
Branch Circuit, Individual. A branch circuit that supplies only one utilization equipment.
Most all manufactures when they want a dedicated circuit are referencing an individual branch circuit. Nothing else served by the branch circuit
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single receptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit
Seems to me it has to do with how "outlet" and "duplex receptacle" are defined. I think of a duplex as two outlets, so a single receptacle would make more sense.
Generally, and in most cases an outlet is where the branch circuit terminates -- J box comes to mind -- fixtures & devices attach to the j boxes -- the manufacture's requirement has nothing to do with a single or duplex being the type of device installed -- If the manufacture called for a 20a dedicated outlet would you query about using a 15a duplex?