Sealing Locknuts

Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
250.97 recognizes a double locknut install as one of the acceptable means of bonding on over 250 volts to ground. How would the use of sealing locknuts affect this ?
(I understand this may have been addressed in '14, but I don't have that Code)
 

Gregg Harris

Senior Member
Location
Virginia
Occupation
Electrical,HVAC, Technical Trainer
250.97 recognizes a double locknut install as one of the acceptable means of bonding on over 250 volts to ground. How would the use of sealing locknuts affect this ?
(I understand this may have been addressed in '14, but I don't have that Code)

It should not have an effect on the continuity. If 250.12 is applied and only one sealing lock nut and one standard lock nut or another sealing are used the continuity would be between the cogs mating with the panel or box etc. and the threads.

The gasket should compress to a depth bellow the cogs.
 