Grounding & lightning Protection for industrial building

Status
Not open for further replies.

TMMB

Senior Member
Location
EGYPT
Occupation
Electrical Manager
we have a building in rectangular shape , but there are 2 sides only available to install the grounding network, can make the grounding/lightning network in two sides only??

also we need separate grounding for low current


please advise
 

Attachments

  • Drawing1 Model (1).pdf
    4.3 KB · Views: 0

TMMB

Senior Member
Location
EGYPT
Occupation
Electrical Manager
the land type is rock, my question is: Earthing for lightning protection should be widespread around the perimeter of the building foot print or can be in single side or 2 sides only ??
 
Last edited:

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
why do you need lightning protection in the first place? and what do you mean by "lightning protection"?

there are plenty of people who have a lot of experience in this rather specialized field that you would be wise to employ to design any lightning protection system, if it is desirable to have one. random people on the Internet is probably not the best place to get this kind of advice.
 

TMMB

Senior Member
Location
EGYPT
Occupation
Electrical Manager
my concern is :the earthing loop conductor should be widespread around the perimeter of the building foot print or can be in single side or 2 sides only ??

lightning protection is required according to the designer recommendations
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
my concern is :the earthing loop conductor should be widespread around the perimeter of the building foot print or can be in single side or 2 sides only ??

lightning protection is required according to the designer recommendations

what do you mean by "designer"? are you talking about the building architect?

the thing is that the questions you are asking really need to be directed to someone competent to answer them. chances are you are going to have to pay to get those answers, since no one here has anywhere near enough information to give you an answer.

it seems to me that you have some options to run a ring around your new building according to the sketch you provided. if you think you need a ground ring no reason you can't extend it around the two small buildings you show in your sketch. you also show space between the new building and the existing buildings where it could potentially go.

the real question is whether or not it is necessary, or even desirable. if it is desirable or necessary, a competent lightning protection specialist can come up with a solution for you.
 
Last edited:

jcassity

Senior Member
Location
24941
my company makes TVSS / SPD systems among many other gear ranging from green energy on out to traditional power. We even have mopeds!

www.alpha.com

Ours is a strikesorb technology and also includes a strike meter with dry contact alarm outputs.

We install a Tier1 TVSS at the MDP or off the ATS.
We instll furhter units downstream as a branch off any desired panel board the customer wants to invest in.

we have single or 3phase units capable of managing Wye or Delta situations.

its in your design, your customer wants it, you know you have to provide it so there you go,, you now can source it at the best cost.
sometimes sittng around asking "why" ends up costing time and money, at the end of the day if your customers design exceeds the AHJ requirements, then naturally the customers standard will be the guidline to follow. Happens to me every single day.,, my customers standards typically exceed the NEC and the AHJ, some inspectors spend a lot of time asking us "why" we over killed the installation.

have fun with the ring..
#2 solid CU ring with cad welds to ground rods approx ever 10' apart which the #2awg sol will be min 30'' below grade or below frost line ~which ever is greater.
Inspection wells flush with the grade and to include cover with test points available and accessable for future fall of potential ring testing to insure a customer desired resistance of (insert number here) or less than 15ohms.
2) #2 solid omni directional feeders coming into your bulding to a newly supplied MGB in which these two wires will be located on opposite sides of the MGB.

for a ground ring certification,,, contact the nation wide coverage company "AETCO", they have performed final acceptance testing for many of my projects.
 
Last edited: