Hey all,
How specifically would you tie into this panel in a Code-compliant manner?
I've done some line side ties (AKA supply side) but the specifics here interest me:
~ Can i land my wires in the line side terminals of the Main breaker?
Cutler-Hammer, Catalog no. BW2200.
~ How can i find out if above is rated for "double lugging", 2 wires in terminal lugs?
~ Has anyone tied into the meter lugs before?
Details:
1. Subpanel more or less inaccessible inside house.:happyno:
2. I beleive this AHJ does not allow load side taps....will check.
3. I got the other stuff; 60A wiring and disco minimum, with fuses rated for my inverter (sma sb5000tl-us, rated ac amps: 22), as close as possible, steel conduit if possible.
4. Splitbolts don't fit on line side conductors, as seen on photo.
How specifically would you tie into this panel in a Code-compliant manner?
I've done some line side ties (AKA supply side) but the specifics here interest me:
~ Can i land my wires in the line side terminals of the Main breaker?
Cutler-Hammer, Catalog no. BW2200.
~ How can i find out if above is rated for "double lugging", 2 wires in terminal lugs?
~ Has anyone tied into the meter lugs before?
Details:
1. Subpanel more or less inaccessible inside house.:happyno:
2. I beleive this AHJ does not allow load side taps....will check.
3. I got the other stuff; 60A wiring and disco minimum, with fuses rated for my inverter (sma sb5000tl-us, rated ac amps: 22), as close as possible, steel conduit if possible.
4. Splitbolts don't fit on line side conductors, as seen on photo.