Would 110.26 workspace clearances apply to terminations at mechanical euipment such as fan cooling units, exhasut fans, etc that are typcially supported from from the ceiling and located above the ceiling?
Thanks.
c
Don't you just love how easy it is to interpret 110.26?
If you want to take it to the extreme, we must have the mentioned working clearances around just about anything you can imagine.
Next step is to take the words "and likely to require examination, adjustment, servicing, or maintenance while energized" and only require working clearance for those items.
But what does that limit you to? Wouldn't crawling thru a crawlspace with tight clearances to go take a voltage or current measurement at a junction box fit this description - and therefore any point where you could potentially take voltage, current or other readings would need to meet the working space requirements.
Many jurisdictions have their own interpretation as to what needs to comply with 110.26 working spaces as the NEC does not define it very well at all, or is such a broad definition that it excludes virtually nothing.