Buccaneer
- Harvey, LA
Trying to trace the path of current on a VFD . The DC bus has +3 & - , that feeds into (2) braking units. The braking units feed a Power Ohm Resistor that has (2) 13,600 watt strips. Each Braking Resistor feeds (1) 13,600 watt section of the Power Ohm. Inside of the Braking Resistor there is a Level Detector that senses across DC + & DC - from VFD. The VFD was energized and within 10 seconds , smoke came from the top. After taking the covers of, we found that the Pre Charge Resistor ( on Vfd )was open. Upon further investigation we found that the Gate Board had also a burnt spot on it. My question is if the DC + and DC - were crossed; without the VFD Contactor pulling in and the motor not running, how did the power make it pass the Transistor ( or through the braking unit ) with reversed polarity and no current to be sensed. This was the first start up on new equipment. Everyone that has seen the drawing of the braking unit diagram said it looks impossible. The braking resistor is a . Any help in understanding this would be appreciated.