I've been asked to price out adding a sub-panel in the basement of a SFD. There is a portion of the basement that has been finished and when this was done there were two 1-1/4" PVC sleeves installed, ~20' each, to be used for future pathways from one side to the other.

I'm going to use #1 SER (AL) to feed the new panel. I don't have the dimensions of the SER in order to calculate conduit fill. My concern is whether or not I can use the existing 20' PVC sleeve for this installation.

Thanks in advance
 

LEO2854

Esteemed Member
Location
Ma
I've been asked to price out adding a sub-panel in the basement of a SFD. There is a portion of the basement that has been finished and when this was done there were two 1-1/4" PVC sleeves installed, ~20' each, to be used for future pathways from one side to the other.

I'm going to use #1 SER (AL) to feed the new panel. I don't have the dimensions of the SER in order to calculate conduit fill. My concern is whether or not I can use the existing 20' PVC sleeve for this installation.

Thanks in advance

If it fits in the pipe,it's fine.

But will it fit in 1-1/4" PVC,LOOK here to get your dimensions.
 