I just corrected 2 subpanels where the the N and EGC were not isolated from one another. The bonding scew was used in one panel and missing from the other. Needless to say I added a ground bar and moved all of the EGC over to the ground bar. Then I removed all of the neutrals removed the bonding screw in the one and checked both for insulation and isolation from ground.
That was obvious. But, on 2 previous occasions the home experienced extensive damage to electronics and appliences amounting to thousands of dollars due to a lightning strike as told be the home owner. In retrospect I strongly suspect that the incorrect wiring of the 2 subpanels contributed to the damage by allowing a surge to appear on both the N and EGC down stream from the SE.
What are your thoughts?
That was obvious. But, on 2 previous occasions the home experienced extensive damage to electronics and appliences amounting to thousands of dollars due to a lightning strike as told be the home owner. In retrospect I strongly suspect that the incorrect wiring of the 2 subpanels contributed to the damage by allowing a surge to appear on both the N and EGC down stream from the SE.
What are your thoughts?