Hello everyone. Trying to understand the 2011 NEC handbook, article 250.30(A) for wye type services and would appreciate your insight:
Typically I would abide by 250.30(A)(1) exception 2 : allowing 4 wires, no ground in PVC between a padmounted transformer and the main disc -- leaving the X0-to-case connection from the factory & installing a MBJ at the main disc. No parallel path.
Now see 2011 NEC whereby they introduce SSBJ, requiring to include a "ground wire" between the transformer and the main disc regardless (if I understand it correctly). Conceivably a parallel path.
(1a) Is SSBJ intended for customer owned SDS (distribution), services, or both?
(1b) Would there be any difference if the padmount transformer feeding the main disc is customer or utility owned?
(2a) Since removing the factory installed X0-to-case is out of the question, are we now required to exclude the installation of a MBJ at the main disc?
(2b) If SSBJ applies to services, how can the term MBJ ever be relevant in a new installation?
(3) It seems to me that NFPA is effectively rendering 250.30(A)(1) exception 2 as worthless because a SSBJ is installed -- yet -- 250.30(A)(1) exception 2 has not been deleted from the code. Whats more, there are still graphs in the handbook depecting a service without any SSBJ (exhibit 250.5)
(4) Minor annoyance, but SSBJ is defined at the beginning of article 250 while SBJ and MBJ are defined in article 100.
Again, any insights would be greatly appreciated. Thanks for reading.