#6 THHN or MC cable = 65 amps, next standard size 70 amp OCPD.
I agree. If we all agree that the ampacity is 65 amps, then you can put it on a 70 amp breaker because it's the next standard fuse size over 60 amp. I reference 240.4(B):
(B) Devices Rated 800 Amperes or Less. The next higherstandard overcurrent device rating (above the ampacity ofthe conductors being protected) shall be permitted to beused, provided all of the following conditions are met:
- (1) The conductors being protected are not part of a mul-tioutlet branch circuit supplying receptacles for cord-and-plug-connected portable loads.
- (2) The ampacity of the conductors does not correspondwith the standard ampere rating of a fuse or a circuitbreaker without overload trip adjustments above its rat-ing (but that shall be permitted to have other trip orrating adjustments).
- (3) The next higher standard rating selected does not ex-ceed 800 amperes.
The standard fuse sizes are found at 240.6(A):
240.6 Standard Ampere Ratings.
(A) Fuses and Fixed-Trip Circuit Breakers. The stan-
dard ampere ratings for fuses and inverse time circuitbreakers shall be considered 15, 20, 25, 30, 35, 40, 45, 50,60, 70, 80, 90, 100, 110, 125, 150, 175, 200, 225, 250, 300,350, 400, 450, 500, 600, 700, 800, 1000, 1200, 1600, 2000,2500, 3000, 4000, 5000, and 6000 amperes. Additionalstandard ampere ratings for fuses shall be 1, 3, 6, 10, and601. The use of fuses and inverse time circuit breakers withnonstandard ampere ratings shall be permitted.