spoonwood45
New member
- Waukee, Iowa United States
What is the proper grounding method of yellow flex csst gas line?
SECTION G2411 (310)
ELECTRICAL BONDING
G2411.1 (310.1) Pipe and tubing other than CSST. Each
above-ground portion of a gas piping system other than corrugated
stainless steel tubing (CSST), that is likely to becomeenergized
shall be electrically continuous and bonded to an effective
ground-fault current path. Gas piping, other than CSST, shall be
considered to be bondedwhere it is connected to appliances that
are connected to the equipment grounding conductor of the circuit
supplying that appliance.
G2411.1.1 (310.1.1) CSST. Corrugated stainless steel tubing
(CSST) gas piping systems shall be bonded to the electrical
service grounding electrode system at the point where
the gas service enters the building. The bonding jumper
shall be not smaller than 6AWGcopper wire or equivalent.
the bonding connection has to be made on solid pipe -- do not attach to the CSST or fitting
I thought it was the black pipe or first CSST fitting. You just could not attach to any portion of the tubing.:?