JDB3
Senior Member
- Location
- San Antonio, Texas
Electric house with the only gas being cook-top, & now the owners are talking about electric demand water heater. For the load calculation, is it kept @ 100% or is d-rating allowed?
If I had to choose an instant water heater for a house with a full family, I would go with a gas unit because the electric ones tend to be under-sized and might require a service upgrade if properly sized.
... I doubt it would run 100% for three hours...
For branch circuit calculations - yes, for service and feeder calculations allowable demand factors are not going to be the same. The cooktop has a specific section for applying demand factors to that type of equipment, the water heater falls more into a "other loads" classification. You may or may not be able to apply a demand factor to the water heating equipment but if you can, it will not be the same method as used for cooking equipment.IMO no difference than a Cooktop as for usage so the load calc would be at nameplate
Others, like mine, instead operate a flow restricter so that you can draw as much water as it can heat to the set temperature and no more than that.the good brands will do the math on flow and compare the input temperature, then they will make an efficiency determination that says,,,
"ok,, i give up,, i cant heat up this many gallons per minute, im just gonna give them "warm" watter".
But given a more complete choice for a full family home, and if I were that concerned about efficiency, my choice would be a heat pump water heater as it is much more efficient than gas and instant types.
Not to derail this thread, but I've always wondered where the cold side goes on these. Is it just dumping cold air into the room with the water tank? If so, doesn't that mean you need to add heat to the room (which could be at a similar efficiency or even worse electric resistance heat)?
That's correct. Placement is key. Some equipment can act as a heat source for a room and reduce the heating demand and increase net efficiency.Not to derail this thread, but I've always wondered where the cold side goes on these. Is it just dumping cold air into the room with the water tank? If so, doesn't that mean you need to add heat to the room (which could be at a similar efficiency or even worse electric resistance heat)?
They are at their best where outside air will work as a heat source all year.
As I may have mentioned before on other threads (or was it another forum?), some if not all on-demand heaters will have temperature regulation problems when working with low flow rates and/or small temperature deltas. Using preheated water can reduce the operating delta easily by a factor of three:It seems to me the best install may be to use a storage type heater to preheat the water to around 100?F, then use an instantaneous heater to gain the remainder of needed heat on demand. That would not lose much heat from the storage tank and would not require as large of a unit to raise the temperature on demand either.
As I may have mentioned before on other threads (or was it another forum?), some if not all on-demand heaters will have temperature regulation problems when working with low flow rates and/or small temperature deltas. Using preheated water can reduce the operating delta easily by a factor of three120-100)/(120-60)=1/3
A storage type heater can work very well with an on-off thermostatic control because of the high thermal mass of water in the tank. But an instant, on-demand, heater must proportion the heat output to exactly fit the amount of water going through per unit time, with no room for clumsy on-off cycles.
An electric heater with PWM controls is most likely to able to handle this, but not all do this. The older units once popular in UK, for example, would have at most two heat settings and you regulated the temperature by controlling the flow rate. Just fine for a tub, but not very safe for a shower.
And a gas source on-demand heater can be even more limited in its low power output range because you cannot safely modulate the gas flame below a minimum level.
Before going down this route, carefully check out the specs of the unit you are thinking of using.
:thumbsup:Good points. I still think there may be some benefit of increasing incoming temperature in places where incoming water is otherwise pretty cold. but maybe the preheating should only be to 75 or 80 degrees at the most. Maybe just an unheated storage tank would gain enough heat on its own in many applications resulting in room temp being the max input to the instantaneous water heater.
I believe NEC requires instantaneous hot water heaters at 100% nameplate for feeder/service calcs. It is a major pain if you are designing a commercial building using solely instantaneous. Maybe your local AHJ allows some diversity. Seems like there should be some allowed, odds of say 10 water heaters firing at the same time for an extended period is quite low.