There have probably been tons of back & forth on similar items,but here it goes.
The fault level on the utility primary is 24,000 A. A new enclosed service main breaker was installed that is rated 65kA and is thus fine.
However, after that breaker, the cables branch off to two main lug only panelboards, with 10kA breakers. All of the breakers are a mix of 1969 vintage GE & Square D. The fault level here is 21,000 A.
These two panels have branch breakers which feed about 20 other panels downstream, all of which are 10kA rated, and are calculated to be overdutied. Some of these panels have main breakers with 42kA, but I can not find any visible evidence that these were series rated. The panels are a wide variety of manufacturers and go back 50 years.
I'm stumped on the next step of ideas to solve this. Am I correct that placing a current limiting fuse at the main entrance would have to be series rated with all of the breakers in the panels through tests? I don't see how anything like this could guarantee that the fuse would clear the fault before any of the other devices start to open.
The fault level on the utility primary is 24,000 A. A new enclosed service main breaker was installed that is rated 65kA and is thus fine.
However, after that breaker, the cables branch off to two main lug only panelboards, with 10kA breakers. All of the breakers are a mix of 1969 vintage GE & Square D. The fault level here is 21,000 A.
These two panels have branch breakers which feed about 20 other panels downstream, all of which are 10kA rated, and are calculated to be overdutied. Some of these panels have main breakers with 42kA, but I can not find any visible evidence that these were series rated. The panels are a wide variety of manufacturers and go back 50 years.
I'm stumped on the next step of ideas to solve this. Am I correct that placing a current limiting fuse at the main entrance would have to be series rated with all of the breakers in the panels through tests? I don't see how anything like this could guarantee that the fuse would clear the fault before any of the other devices start to open.