Load is a continuous 200A, size the conductors and OCPD based on 125%. So per code installation will be:
200 x 1.25 = 250A
Size of the conductor is 310.15(b)(16) is 250kcmil
OCPD is minimum 250Amps.
So far so good.
I know why the OCPD is based on 125%.
My question:
So since the conductor in table 310.15(b)(16) is based on continuous ampacity, then why does the conductor has to be sized to 125% if it will never see any load higher than 200Amps anyway.
3/0 conductor is good for 200 continuous amps, all the breaker can continuously deliver is 200Amps, all the load will ever be is 200Amps. So why size the conductors to 250 Kcmil?
Thanks.
200 x 1.25 = 250A
So far so good.
My question:
Thanks.