I have to put a small 22kw gen on a roof.  I've never done this.  What kind of base do I need?
In addition to loading, I would thoroughly check out vibration isolation. Most generators are designed to be mounted on concrete floors or separate pads, and putting one on a roof might well require additional vibration isolators, not just a flexible raceway section.On first view it seems you need a PE but let's see what we can do for you and your client first. Please describe the building and the roof structurally. And how high is this?
You're pretty much doing what a HVAC contractor does with a package unit or chiller, and he needs an engineer.
IMHO, without adding vibration isolators to the standard generator assembly it would have been pretty bad. But that may vary from manufacturer to manufacturer and model to model.I called a structural engineer to look at the ceiling support. He drew up plans to support the extra weight. It required welding extra supports to the bar joists. Four posts that would go thru the roofing to a frame to fit the gen base. My welder had made up the frame and the project got canceled.
I wondered how much noise and vibration there would have been.