ok... 1,200 amp 480 service 3 phase, 4 wire.
nema 3R with a pull section, obviously. on a slab, out in the open.
edison vault feeding it is about 80' away. 8' x 10' pad with substructure.
now, for the secondaries, three 4" pvc would do. what
edison wants is four 5" conduits, in concrete, with no less
that TWELVE FOOT (12') radius sweeps and 90's.
the primary is one single 5", with 12' radius 90's and sweeps.
when did this 12' radius thing start?
btw, the edison print show four 750 aluminum in one conduit for
the service entrance conductors. and three spares.
you guys dealing with SCE regularly, is this normal?