Large paint booth using 10 HP exhaust fan. Booth is two years old.
First motor had trouble starting and was replaced.
This motor is having similar problems. Don't know the time frame but installer said it did work fine in the beginning.
Facility served by REA single phase 7.2kV through 37.5 kVA transformer, 240V secondary.
Short 4/0 al. triplex to the building to serve 400 amp main. Everything else in the facility works fine.
50 amp DP breaker serves approx. 80' run of # 8 cu stranded in conduit to starter and then up through the roof to the motor.
Have not seen motor data plate.
Motor will eventually start and run but seems to stall on the first couple attempts producing 190 amps. Push the stop button when it stalls and start again until motor runs at 29 amps.
Voltage measured at start of wire run on breaker and voltage falls from 245 to 235 during stall.
Make same test at starter during stall and voltage falls from 245 to 210.
When motor is running at 29 amps the voltage drop is 1%.
They are prepared to replace the motor again but looking for explanations of starting problems.
Voltage drop calculations using measured running amps work with the #8. They have replaced the two start capacitors hoping that would make a difference. Didn?t know if they were bad, just changed them.
Is there a design problem?
Option is to change to inverter, VFD and 3phase motor.
They have installed 10hp single phase motors in paint booths elsewhere and haven't seen this before?
First motor had trouble starting and was replaced.
This motor is having similar problems. Don't know the time frame but installer said it did work fine in the beginning.
Facility served by REA single phase 7.2kV through 37.5 kVA transformer, 240V secondary.
Short 4/0 al. triplex to the building to serve 400 amp main. Everything else in the facility works fine.
50 amp DP breaker serves approx. 80' run of # 8 cu stranded in conduit to starter and then up through the roof to the motor.
Have not seen motor data plate.
Motor will eventually start and run but seems to stall on the first couple attempts producing 190 amps. Push the stop button when it stalls and start again until motor runs at 29 amps.
Voltage measured at start of wire run on breaker and voltage falls from 245 to 235 during stall.
Make same test at starter during stall and voltage falls from 245 to 210.
When motor is running at 29 amps the voltage drop is 1%.
They are prepared to replace the motor again but looking for explanations of starting problems.
Voltage drop calculations using measured running amps work with the #8. They have replaced the two start capacitors hoping that would make a difference. Didn?t know if they were bad, just changed them.
Is there a design problem?
Option is to change to inverter, VFD and 3phase motor.
They have installed 10hp single phase motors in paint booths elsewhere and haven't seen this before?