 - Placerville, CA, USA
 - Retired PV System Designer
Like a broken watch, it is right twice a day. Once a day if you have the watch in 24 hour mode.
Tapatalk...
			Tapatalk...
Really the fall of potential method uses the same principle as behind the fuse breaker method, but more accurately and above all, safely.Would it suffice to say using the light bulb (or fuse for that matter) test just doesn't give us the info we are looking for?
Use a sufficiently low voltage secondary isolation transformer for low output current such as used by a meggar.If you totally isolate you don't get the same results as you are not connected to the utility MGN network so it is not the same test.
If you are not interested in the reasons behind it, that is a fair summary, yes.
I might tweak it slightly to say that the method does not always give the information we are looking for. (And you can't tell when it is right and when it is not.)![]()
I believe that the concept that you are looking for is 'resistance to distant earth'.
The exact resistance will depend upon the distance between the electrodes and the material between them. In theory you could make a graph of resistance versus electrode distance.
The resistance of a conductor increases with length and decreases with cross section. In the case of current flowing through the earth, the 'cross section' is a bit difficult to define; the earth is huge but your electrodes are small. What happens is that current has to spread out into the earth from your tiny electrodes.
Roughly, the further apart your electrodes are, the further the current can spread, and the larger the effective cross section of the earth carrying your test current.
The net result is that your graph of electrode-electrode resistance versus spacing will asymptotically approach some fixed value as the spacing gets large. (Assuming that the characteristics of the individual electrodes don't change as you move them.....)
With this in mind, you can _define_ the resistance of a single electrode as the resistance between that electrode and a (fictional) zero ohm electrode infinitely far away.
The resistance between any two electrodes that are sufficiently far apart is then given by the sum of the two resistances as defined above.
This is not reality; you could never have a zero ohm electrode and the earth is only of finite size. But it is a useful fiction to provide a baseline for assigning values to individual components.
In much the same way voltage is _always_ measured between two points, but if you select an appropriate reference zero (even a fictional one) you can assign voltage values to individual points and use those values in your calculations.
-Jon
The point is that measured over long distances the resistance of "the earth" really is zero.
Between any two points the area through which the charges flow increases faster than the distance separating those two points.
The resistance we assign to each ground electrode takes into account the steadily decreasing resistance of each spherical shell around it.
The result is that if the electrode resistance is measured properly the electrode to electrode resistance will be equal to the sum of the two resistances.
Or, if they are close enough that the significant zones overlap, the resistance will be LOWER.
Tapatalk...
What I am hearing is that the earth has 'negative' resistance. Instead of resistance increasing with distance, it decreases. Likely due to the addition of parallel paths possible vs. the number of series paths?
I disagree.
FOP is testing electrode to earth resistance. The 'fuse breaker' method gives you electrode to POCO neutral resistance. The two may or may not be the same. I'll bet mostly not as the POCO electrode system is now part of the equation and for testing disconnected electrodes we don't want it to be part of the equation.
If we connect any charged object to earth, it loses its charge. By earthing an object, we ensure that it does not give an electrical shock.I take it that the electrical point we refer to as 'the earth' exists only mathematically. Unless it's a point on the molten nickel in the center.
Any sufficient large metal object may be used as 'earth' electrode.Is there a standard electrode somewhere? One to calibrate test equipment by?
If the object in question is connected to a voltage source, earthing it does nothing more than raise a small section of the earth around the grounding electrode to that of the object. It really does nothing to prevent a shock, unless you are standing on or very close to the grounding electrode.If we connect any charged object to earth, it loses its charge. By earthing an object, we ensure that it does not give an electrical shock. ...
I've always wanted to try this with a ground rod system : take a pigtail light socket, screw in a 5a fuse, wirenut it in series to a 1-pole breaker and the GEC (which has been disconnected from the bussbar and any grounded metal in the panel), turn on the breaker and see if it blows the fuse. Quick and dirty test to see if it makes 25 ohms![]()
"You are quite correct that if you have two '5 ohm' ground electrodes, and measure the resistance between them, the result will be something different than 10 ohms."
Conflicts with:
"With this in mind, you can _define_ the resistance of a single electrode as the resistance between that electrode and a (fictional) zero ohm electrode infinitely far away."
[/QUOTE]"The resistance between any two electrodes that are sufficiently far apart is then given by the sum of the two resistances as defined above."
Is FOP testing not an extrapolation of values, as opposed to a single measurement taken as an accurate value?
Nowhere ohms law is violated (save non-linear circuits). Some resistance/impedance might have been missed in Mike's experiment.Mike Holt has done just that and its available on a video. He drives a ground rod, checks the resistance with a fall of potential meter, clamp on meter and and measures the current at 120 volts.
Current > ohms law follows the meter readings.
If the charge on a metal object from a voltage source is steady, earthing the object will free one from receiving a shock on touching near or remote from it, provided the other terminal of the voltage source is not earthed. Metal objects with fluctuating charges are liable to give electrical shocks when there is considerable earth resistance.If the object in question is connected to a voltage source, earthing it does nothing more than raise a small section of the earth around the grounding electrode to that of the object. It really does nothing to prevent a shock, unless you are standing on or very close to the grounding electrode.
And don't ask me what I think of you; I might not give the answer that you want me to.If you are not interested in the reasons behind it, that is a fair summary, yes.