I work in an industrial facility, in one of the buildings we have a 20kw 480v 3ph heater in 2 corners. The nameplate states 24.4 full load amp. They share a 60amp breaker. 3 number 6 wires leave the breaker to a junction box perhaps 50 feet away. Then the number 6 wire is spliced to number 10 wire that then feeds the heaters perhaps 30 feet away. Near the heaters are 30amp fused disconnects. I happened to look inside one of the disconnects the other day and noticed that the top of the disconnect has been very hot causing some plastic to melt and the insulation on the number 10 wires on the line side of the disconnect was charred away for an inch or 2 and the tops of the fuses were very black. The wires on the bottom of the fuses looked normal. So seeing this I decided to look at the other heater disconnect and it was in just as bad a shape as the first one. The heaters have been in service like this for 20 years. Looking at article 424 I'm not sure if the wiring method is to code or not. Can 2 heaters this size be fed from 1 60 amp breaker? Was it ok for the number 10 to be spliced to the number 6 and ran to the disconnects?
I know this was long winded but I'm hoping with this much detail someone will know exactly what I should do.